For whatever it is worth,
AWWA Manual M31, Distribution System Requirements for Fire Protection (3rd edition 1998) included substantial discussion of “Fire Flow Requirements” and also contained the verbiage, “…meeting requirements for minimum pipe sizes (e.g. 6-in. [150-mm] pipes in loops and 8-in. [200-mm] dead ends) in neighborhood distribution mains when much smaller pipes would suffice for delivery of potable water only.”
The “Ten States Standards” (Recommended Standards for Water Works) 2007 Edition under section 8.2.2 Diameter included,
“The minimum size of water main which provides for fire protection and serving fire hydrants shall be six?inch diameter. Larger size mains will be required if necessary to allow the withdrawal of the required fire flow while maintaining the minimum residual pressure specified in Section 8.1.1.
The minimum size of water main in the distribution system where fire protection is not to be provided should be a minimum of three (3) inch diameter. Any departure from minimum requirements shall be justified by hydraulic analysis and future water use, and can be considered only in special circumstances.”
NFPA 24 Standard for the Installation of Private Fire Service Mains and Their Appurtenances (1995 edition) contained, “Adequacy of water supply shall be determined by flow tests or other reliable means…” and “…Public mains shall be ample size, in no case smaller than 6 in. (152 mm).”
While as others have quite eruditely stated there might be some new construction with perceived scopes outside these particular standards of care that allow smaller pipes; however, about the only other thing I would add is that there are quite large quantities of 6” and particularly smaller water distribution piping now being replaced at substantial cost/ at least in the United States (much with 8" and larger pipes), not necessarily that they are unsuitably ag(e)ing [perhaps the most popular perception] or not providing cost-effective service, but instead due to the fact they simply cannot (with encountered burgeoning growth etc.) provide the level of flow that is now deemed necessary for now developed areas.
I guess virtually all those original designers also thought the pipes they specified would be large enough for their lives as well (many originally quite "rural" areas have quite rapidly become quite developed)! [Incidentally, if anyone is aware that any of this standards etc.verbiage has changed in more recent versions, feel free to post the latest).