Great thank you all for your responses. I think it's the shortage and availability at this point of construction. It has to be shipped for little further and time delays and construction schedule. It was also the client's request to check for alternates.
found these options: but nothing like this defined in ACI or such articles.
403S.8 - Mix Design Options
For the structural concretes identified in Table 5 (Classes C, H and S) and any other class of concrete designed using more than 520 lbs. of cementitious material per cubic yard (310 kgs per cubic meter), one of the mix design options presented below shall be used.
For the non-structural concretes identified in Table 5 (Classes A, B, D and I) and any other class of concrete designed using less than 520 lbs. of cementitious material per cubic yard (310 kgs per cubic meter), one of the mix design options presented below will be used, except that Class C fly ash may be used instead of Class F fly ash for Options 1, 3 and 4 unless a sulfate-resistant concrete is required.
A.Option 1: Twenty (20) to thirty-five (35) percent of the cement may be replaced with Class F fly ash.B.Option 2: Thirty-five (35) to fifty (50) percent of the cement may be replaced with ground granulated blast-furnace slag.C.Option 3: Thirty-five (35) to fifty (50) percent of the cement may be replaced with a combination of Class F fly ash, ground granulated blast-furnace slag or silica fume. The combination may not include more than thirty-five (35) percent fly ash and no more than ten (10) percent silica fume.D.Option 4: Type IP or Type IS will be used and up to ten (10) percent of the cement may be replaced with Class F fly ash, ground granulated blast-furnace slag or silica fume.E.Option 5: Thirty-five (35) to fifty (50) percent of the cement may be replaced with a combination of Class C fly ash and at least six (6) percent of silica fume, ultra fine fly ash or metakaolin. The combination may not include more than thirty-five (35) percent fly ash and no more than ten (10) percent silica fume.F.Option 6: A lithium nitrate admixture will be added at a minimum dosage of 0.55 gal. of thirty (30) percent lithium nitrate solution per pound of alkalis present in the hydraulic cement.G.Option 7: When hydraulic cement only is used in the design, the total alkali contribution from the cement in the concrete does not exceed 4.0 lbs. per cubic yard, when calculated as follows:
alkali (lbs. per CY) = .01 (lbs cement/CY) (% Na2O equivalent in cement)
where (% Na2O equivalent in cement) is assumed to be the maximum cement alkali content reported on the cement mill certificate.