QUESTION 1: Why transformers have a greater inrush multiplier when back feeding through it….
ANSWER 1: According with the transformer committee of IEEE/PES, there are significant inrush current differences when back feeding a transformer. Below is a summary of the inrush range multipliers based in the nominal full load rated current.
Peak Inrush Current in PU of Nominal Current for Power Transformer
Without External Impedance.
-----------------------------------------------------------------------------------------
DESCRIPTION STEP-UP STEP-DOWN
-----------------------------------------------------------------------------------------
Delta connected primary 30-45 19-25
Grounded Y Primary 50-60 30-35
-----------------------------------------------------------------------------------------
Please notice that the above values are for step-up and step-down units. However, the similarity with a single transformer still applies.
QUESTION 2: ….the inrush multiplier is higher say 10, than normal inrush currents i.e 3-5??
ANSWER 2: Beware that inrush is a random factor that primarily depends on the point of the voltage waveform at which the switch/breaker closes, as well as on the sign and value of the residual magnetic flux in the transformer core.
The rms inrush current is a fraction of the peak values determined in a particular period of time. For instance, the “standard” rms inrush points multipliers of transformer (rated) full-load current are: 35x, 12x, 6x, 3x, at 0.01, 0.1, 1.0, 10 seconds respectively.
QUESTION 3: Any reason why it happens (Why transformers have a greater inrush multiplier when back feeding through it…).
ANSWER 3: The above results shows that the inrush current are higher if the transformer is energizing from the LV side regardless the type of connections with higher values for grounded Y primary configuration.
One possible reason is the core will be saturated easier if energized from the low voltage side were the high current occur. Keeping in mind the magnetic flux increase with the current.