L775,
Don't ignore what Lutfi asked. If you have that much water, you eventually have to temporarily dewater the site to build the basement slab and foundation walls. So, you will need sheeting (essentially, a cofferdam). If the sheeting can be driven deep enough, you may not need a tremie seal. Since you have to control the flow of water from all directions (a tremie only controls the vertical flow), you will need sheet piling or some other more expensive cut-off wall (deep soil mix walls or slurry walls) around the perimeter to control the horizontal flow of water. You could also install a dewatering system such as deep wells or well points. The proper solution to your problem depends greatly on the subsurface conditions (soil layer types? rock?) and on the closeness of any adjacent structures. Also, investigate the need for underpinning any adjacent buildings, if any.
Make sure that the building's basement floor slab is properly attached to the tremie concrete or that the slab is held down some other way (tiedown anchors?) to prevent uplift from water pressure.
For a job in Florida, call Moretrench American Corporation, 973-627-2100, in New Jersey. Moretrench has a Tampa office but I would start with their office in New Jersey. They specialize in dewatering, earth support systems, and ground anchors (tiebacks and tiedowns).