Transmission line capacitance (charging) in VAR

Status
Not open for further replies.

chuckd83

Electrical
Joined
Oct 2, 2014
Messages
43
Location
US
I am looking at calculating line capacitance / line charging in VAR or VAR/mile for a HV line. Not charging current. I find plenty of sources on what it is, but not how to calculate it. I have the transmission line parameters such as R, X, and Y.
 
You need B. It's a geometry problem similar to solving for R. Most Power System Analysis texts should include a section on calculating line capacitance.
 
I believe I have that with Y which is the charging susceptance. It is given in siemens. How does this translate to VAR? Is it simply V(L-L)^2 * Y?
 
Ichg = YVan

Qa = YVan^2

Where G = 0 and Y = j*2*Pi*f*Can
 
ATP-EMTP has a calculator for line parameters if you don't want to do it by hand and it is free.

------------------------------------------------------------------------------------------
If you can't explain it to a six year old, you don't understand it yourself.
 
Y is the inverse of Z (R + jX). The units may be the same as Y, but G + jB is very different than Y.
 
See the graph below from the IEEE Std

Line_Charging_Current_rdscrc.jpg
 