MJC said:
If the reinforcement was centered on the 8" wall all the way up or sloped gently at the transition, would you still be worried about the compression portion of the flexure at that joint? I.E. check bearing only on the ends and the web like Fletch10 mentioned or confirm the 12" CMU wall is solid grouted at the joint?
I'd definitely give the compression situation some attention. If your bars are off center in the 12" block (unlikely), one interesting consequence of that is that your bending strength will be greater for outward wind pressure than inward wind pressure. That, because your flexural resistance would be working over a larger lever arm. This affect may well negate the impact of delivering your compression force to the webs of the 12" block rather than the inside face shells.
With regard to the top course(s) of the 12" block being grouted, I struggle with deciding how much I personally would want to rely upon that. There are numerous instances in masonry construction where we implicitly rely on a loaded chunk of grout to not slide through the open cores below when loaded in compression. At the same time, there's no explicit check available for that to my knowledge. So I acknowledge that there's a mechanism there but am personally reluctant to rely upon it.
MJC said:
I'm curious if you have any recommendations for a concrete design textbook?
Do I
ever. I fear that modern textbooks will be the death of us because few to none of the popular ones seem to adequately deal with the all important subject of detailing well. For the most part, I think that they're geared towards being used as college textbooks and, thus, sales. Undergraduate coursework usually doesn't touch this stuff and graduate coursework rarely does either, at least not in any detail. Here's what I recommend:
Toward a Consistent Design of Structural Concrete - Schlaich Freebie!
Detailing of Reinforcement in Concrete Structures - Gilbert Freebie!
Reinforced Concrete Structures - Park & Paulay
I know, it sounds nuts to buy and read an antique book from 1975 written by New Zealanders. It's not your code, it's outdated by half a century, and it was written before anybody was even using the terminology "strut and tie" regularly. You'll just have to trust me on this. To my knowledge, this book has no meaningful competition with respect to setting out the fundamentals of first principle concrete design. To read it is to feel as though you are walking a path set out for you by gods, placing your tiny mortal feet inside each size 36 footprint as you go. It took me a solid nine months to read the whole thing. If Alzheimer's has a silver lining for me, it will be that perhaps I can read the book over again with fresh eyes and once again know the rapture that was those nine months.
Lastly, if there's anything that I can personally help you with in this regard, feel free to contact me directly. It's pretty much my favorite topic in all the world. A peak at my Eng-Tips profile and a little resourcefulness would facilitate contact.