Check the transformer rating plate.
Transformers connected to 415V buses usually have a no-load secondary terminal voltage at centre tap position of 433V.
ie. Transf secondary current rating I LV = 1.6*10^6/( sqrt(3)*433 ) = 2133 A
As mnewman says, the current rating is based on the no-load voltage. You need to check the no-load voltage quoted on the transformer rating plate. Typically this will be 433 V so I would agree with mnewmans value of 2133 Amps as the rated current of this winding.