Your are right, I should have read your response more carefully.
The whole discussion that I started with my first post, was not about the "actual ohmic impedance", but the Z%. Please review my first post. But now that you mentioned this "actual ohmic impedance", I realized that I have less knowledge in this subject that I thought. Here is why.
The Z% (in a specific power base, normally the nominal kVA) is used to calculate the short-circuit current when using the PU method or in software packages like SKM. Not the "actual ohmic impedance".
Knowing this Z% (per cent) you can convert this impedance in Per Unit on the selected base power and then covert it to the "calculated ohmic value" at the primary of secondary voltage using the per unit calculations.
Lets assume that Z%1 is referred to the nominal kVA and Z%2 is referred to the full- load kVA.
Now we can obtain the "calculated ohmic value" of each one of these percent impedances (Z%1 and Z%2)using the PU calculations as you stated in your response. Since Z%1 and Z%2 were different at the start, their "calculated ohmic values" will also be different.
The short-circuit calculations should be based on the Z% values (if you use the PU method) or the calculated ohmic values of the Z% (if using the ohmic method).
Here is where I am confused. I kind of agree with you that the "actual ohmic impedance" you mentioned in your response should not change depending on the base kVA chosen because the transformer construction remains the same. But the "calculated ohmic value" of the Z% do change depending the base kVA. The question therefore is:
Are the "calculated ohmic values" (obtained from the PU calculations starting from the Z% impedance) the same as the "actual ohmic impedance" you referred in your response?
If it is, something is wrong. They can't change and not change at the same time.
If it is not, what is the difference between the "actual ohmic impedance" and the "calculated ohmic impedances" based on the Z%?
Does the manufacturer publish this "actual ohmic impedance"? It does publish the Z%.
I know I am missing the magic link to put these two concepts together. Therefore, if you have a reputable reference (like and IEEE publication) that zooms in this problem specifically, I would appreciate if you or any other engineer following this thread can send it to me.
Thanks