I would like to thank all for the valuable comments .
Regarding doubt in sampling these values are after repeating sampling, we are very familiar with DGA sampling so no doubt on this subject.
The size of transformers as follows:
1. 2000 kVA 34.5 kv/480 V Sealed type transformer we found Acetylene in the three samples.
3ppm , 3ppm , 2.5 ppm
2. Other transformer rating 2500 kVA , 4.16kV/480V conservator type transformer with breather we found only Ethane C2H6 (sorry for initial mistake I mentioned in the beginning , It is not C2H4 the gas found is C2H6 )
158 ppm , 96 ppm , 117ppm
No welding done on units .
Transformers located / installed in Petrochemical company “ethylene and polyethylene plant”
Is there any possibility that this could be the reason? The gas are coming from outside environment since transformer is conservator type? If yes how we can solve this issue?