The first time I designed a tower crane foundation (tcf), my boss had me look at this for my own benefit. For an embedded spread footing, you get so much mass that between friction on the base and passive resistance on the sides(due to the base section anchors, most of these foundations are at least 4' deep, with 6' being normal), it's really not a controlling limit state for the design. Granted, all the tcf's I designed had the sides backfilled and compacted with some good granular soil. If it's a spread footing sitting on the surface, then you should definitely pay special heed to the friction req'd and spec a material underneath that can develop the friction factor you need. By far, for a spread tcf, the overturning moment about the diagonal controlled the length and width required. The "cranes and derricks" book that Chicopee referenced covers the analysis of that condition.
Of course, if your tcf is supported on piles, you can pass the torsion directly to the piles as shear.