Thanks for all the information. What I was able to find:
NESC 384 C: Bonding should be provided between all aboveground metallic supply and communications enclosures that are separated by a distance of 6 feet or less. For the purpose of this rule, pole grounds are not required to be bonded to the communication enclosure.
IEEE 80: Substantial metal-to-metal touch voltages may be present when a person standing on or touching a grounded object or structure comes into contact with a metallic object or structure within the substation site that is not bonded to the ground grid. Calculations of the actual metal-to-metal touch voltage are complex. In practice, hazards resulting from metal-to-metal contact may best be avoided by bonding potential danger points to the substation grid.
It is impractical, and often impossible, to design a ground grid based on the touch voltage caused by the external transferred voltages. Hazards from these external transferred voltages are best avoided by using isolating or neutralizing devices and by treating and clearly labeling these circuits, pipes, etc., as being equivalent to energized lines.
OSHA: The employer can use a grounding grid to equalize the voltage within the grid or bond conductive objects in the immediate work area to minimize the potential between the objects and between each object and ground. (Bonding an object outside the work area can increase touch potential to that object, however.)
OSHA also referenced ANSI C2 which is NESC as above.