Suggestions/Comments on: </images/new.gif> eeguy (Electrical) Jun 10, 2001 posting marked by ///\\I understand that an SRC based AVR must conduct (or fire the field) for some "appropriate" portion of a half wave to regulate the generator output voltage, but...For a "generic" half wave AVR on a self excited 3 phase generator, is there a particular instant in time with regard to the phase of the output voltages that is optimal for firing the field?
///Generally, the AVR must control its output (DC) to the speed governor and to whatever else this output may be used for. Therefore, the AVR output is sensing the generator output voltage (or possibly from other source providing a correct and suitable voltage reference) and processes it by changing the firing phase angle proportionally to the generator voltage output. There are control loops involved with control blocks with various constants to have the genset delivering the generator output nominal voltage at nominal frequency within designed tolerances.\\Or, can the firing be totally asynchronous to what's going on in the generator (as would be the case if the AVR derived its power from some "unrelated" AC source)? Why does, or doesn't it matter? Also, Would the answer be any different if the generator were paralleled to another generator vs driving a load standalone?
///Generally, as in any feedback control loops, the reference point or setting must be used. How it is accomplished, that is a different question. However, the generator output voltage and frequency monitoring for its control purposes is mandatory, to achieve the specified generator output voltage and frequency. There is some manufacturer literature available at:
type Regulators: Voltage the will return 194 companies to obtain more info about voltage regulation.
Books:
1. Bergen A. R., "Power Systems Analysis," Prentice-Hall Inc., 1986, Chapter 11 "Voltage Control System"
2. Fitzgerald A. E., Kingsley Jr., C., Umans D. D., "Electric Machinery," Fifth Edition, McGraw-Hill, Inc., 1990, Page 581 Par. b. Turbine-Generator Excitation Systems
It addresses both options, i.e. either input voltage reference from the generator output or from a separate voltage source for voltage reference purposes.
If generators are in parallel, then additional requirements are usually in effect, e.g. load sharing, voltage and speed(frequency) regulator droops, etc.\\