You could double-check the computer output by:
1. Apply the weight of the building laterally
2. Run a static analysis
3. Get the deflection, Delta, in inches at the top
4. Natural frequency approximately equals 0.18*sqrt[ (386 in./s2) / Delta ]
5. Natural period = 1 / Natural Frequency
When I've done this, the result has been pretty close, so it's a good sanity check on the computerized analysis.