Thank You @ Kiribanda
Thank You for sharing your knowledge and expertise.
The nameplate of the PCB used the IEC 62271-100. While using 0.037sec the asymmetrical current exceeds the device capability as well as Idc exceeded.
Anyways, the system where I did its short circuit calculation has 72.5kV PCB with 25kA breaking current and 65kA making current with 44% dc component rated in IEC standard which is used in the 69kV line, the 13.8 kV line used 15kV vacuum circuit breaker with rated short circuit current of 25kA, the rating used ANSI standard. Since the system used both ANSI and IEC standards. I'm confused about what standard I will use in my short circuit calculation. I tried using only ANSI standard calculation for the whole system. What will I do in my short circuit calculation? What Standard will I used in the computation?
Attached here is my result in ETAP using 0.037 sec as minimum time delay,.
Will I used only the symmetrical breaking current result or the asymmetrical breaking current to compare with the nameplate breaking current?
How can I evaluate the result based from the short circuit rating in the nameplate?