Good afternoon;
Could someone assist me in verifying my calculation? Or point me in the right direction to a reasonable estimation?
I am attempting to work out a decent mathematical model for cooling round solid rods on a cooling bed. The material needs cooled from a high of 700*F to 150*F with a max summer temp of ~90*F.
Cooling bed 150' x 40'
Aluminum rods in 3,5,8"
Up to 120' length
Delta T 450*F
I have a possible solution available currently.
#1 up to 6 individual fans at 34K cfm 1.75"wg spaced every 20' blowing perpendicular to the rod as a fin.
I performed a mass comparison:
Mass of 20' section in size of 3,5,8"; times specific heat divided by ration of temps.
Mass of fan times specific heat.
I divided the total heat required by the fan total cooling capacity which gave me:
2" 3 min.
5" 16 min.
8" 41 min.
I can't use water per customer requirements. The cooling bed is the most open location which supports our plans. I wish to follow KISS which leads us to forced air cooling.
Thanks
Rich
Could someone assist me in verifying my calculation? Or point me in the right direction to a reasonable estimation?
I am attempting to work out a decent mathematical model for cooling round solid rods on a cooling bed. The material needs cooled from a high of 700*F to 150*F with a max summer temp of ~90*F.
Cooling bed 150' x 40'
Aluminum rods in 3,5,8"
Up to 120' length
Delta T 450*F
I have a possible solution available currently.
#1 up to 6 individual fans at 34K cfm 1.75"wg spaced every 20' blowing perpendicular to the rod as a fin.
I performed a mass comparison:
Mass of 20' section in size of 3,5,8"; times specific heat divided by ration of temps.
Mass of fan times specific heat.
I divided the total heat required by the fan total cooling capacity which gave me:
2" 3 min.
5" 16 min.
8" 41 min.
I can't use water per customer requirements. The cooling bed is the most open location which supports our plans. I wish to follow KISS which leads us to forced air cooling.
Thanks
Rich