muuddfun

Geotechnical
Feb 4, 2008
107
What amount of differential settlement do you find to be the tolerable limit for typical tilt up concrete construction? What would you have typicaly for footing loads?
 
Replies continue below

Recommended for you

i usually see the 1/2 to 3/4 inch tolerable differential number thrown out by structural engineers on jobs i've worked on.

4-5 klf for say a warehouse. maybe higher for other applications.
 
What would you use for isolated interior columns, load and settlement?
 