Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Ties at anchor bolts

Status
Not open for further replies.

EBF

Structural
Joined
Jun 2, 2003
Messages
62
Location
US
Are ties required to enclose anchor bolts at frame column footings? Can anyone direct me to a code reference on this? I found a reference for anchor bolts embedded in concrete columns (2001 CBC Section 1921.4.4.8), but i couldn't find anything similar for anchor bolts at steel to concrete footing connections...
 
NO.

But, make sure the loads don't pull the anchor bolt out. ACI 318-2002 (and the IBC 2000) has an appendix that give a method to check this.
 
EBF

The anchor bolts are tied to the rebar mat(s) and a wooden template may be used to maintain horizontal and vertical spacing. Since the bar spacing at columns is usually decreased, why not design the mat to locate the anchor bolts at the desired locations.

Hope this helps. [cheers]
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top