asiem
Structural
- Nov 19, 2003
- 6
I have been looking at a one story addition to a house that was built without a structural engineer and is now having problems. The addition is conventional wood light framed construction with 9' 2x6 walls supporting 2x10 rafters at a 4:12 pitch over a total building width of 28'. The rafters are collared with 2x6s about 3' above the eave height (12' above the floor) creating a tray ceiling. My analysis shows the rafters failing and this configuration has, of course, created thrust on the exterior walls which have now begun to bow under dead load alone. Normally under these circumstances I would recommend that a strucutural ridge beam be installed, however, the architect does not want to go this route because of accessibility concerns. Instead, what we are looking at doing is reinforcing the rafters. I can get the rafters to work by sistering each. My quesitons is what to do about the horizontal thrust. A finite-element analysis run pin-roller shows the frame with sisters deflecting 1" in the X-direction vs. 2" without sisters. This seems alot better but keep in mind that the present deflection has occurred under dead load only. I'm worried that if all we do is reinforce the rafters the thrust will be just as bad under full loading conditions as it presently is under dead load only. Any thoughts?