metta0810
Electrical
- Jul 24, 2009
- 13
I have three-single phase transformer, each is rated at 250kVA, 34500-2404x7212/12490Y.
The name plate shows if the secondary side is connected in series the voltage is 7212V, 34.7Amps. If the secondary is connected in parallel the voltage is 2404V, 104 amps.
The impedance shows as 5.15% at 34500-7212 VOLTS.
The secondary side of the three-single phase transformer is connected to 2.4kV Bus.
Since, the impedance is obtained based on 34500-7212 Volts, Do I need to convert the impedance based on 34500-2404? If so, how do I convert the impedance?
Thanks.