ffont
Electrical
- May 4, 2010
- 23
There is an application for a GrdY-GrdY bank using 3 single phase transformers 14.4kV-120/240 into a 24.9kVGrdY-208GrdY bank.
2 of the units are 100kVA, with an 1.8% Iz and both will have their 120V LV winding paralleled; the third transformer is a 200kVA, same voltages, 2.2% Iz but only 1 of the 120V LV winding is used for making the third leg of the secondary Y, while the other 120 LV winding is feeding a separate single phase load at 120V.
For voltage unbalance I need to compare %Iz on each of the 3 legs. Do I need to compare the 1.8% Iz value of the two 100kVA units with the half winding %Iz of the 200kVA part of the 3 ph bank? There will be time when the 1 ph load is very low.... but at other time the 1 ph load could be higher than 50kVA.
Given that the full winding %Iz of the 200kVA is 2.2%, what would be the half winding %Iz to use for comparaison?
2 of the units are 100kVA, with an 1.8% Iz and both will have their 120V LV winding paralleled; the third transformer is a 200kVA, same voltages, 2.2% Iz but only 1 of the 120V LV winding is used for making the third leg of the secondary Y, while the other 120 LV winding is feeding a separate single phase load at 120V.
For voltage unbalance I need to compare %Iz on each of the 3 legs. Do I need to compare the 1.8% Iz value of the two 100kVA units with the half winding %Iz of the 200kVA part of the 3 ph bank? There will be time when the 1 ph load is very low.... but at other time the 1 ph load could be higher than 50kVA.
Given that the full winding %Iz of the 200kVA is 2.2%, what would be the half winding %Iz to use for comparaison?