It's been a while since I last dealt with generators and 3-phase - so need a refresher (and an electrical engineer that I've been trying to hire!!!).
I have current demands for each phase of a load on the generator (say, a motor). If I were to work-out the individual phase power, it is = V(line) * I (line).
If I am confirming the size of the 3-phase generator for the load, how would I calculate the 3-phase equivalent power?
Is it
a) P = sqrt(3) * V(line) * I(line); or
b) P = sqrt(3) * V(line-line) * I(line)
line voltage is 220, and line-line voltage is 440V. I(line) would be the calculated maximum demand any one of the lines.
Sorry, such a high-school question, but as they say, don't use it, you loose it.
It's been a while since I last dealt with generators and 3-phase - so need a refresher (and an electrical engineer that I've been trying to hire!!!).
I have current demands for each phase of a load on the generator (say, a motor). If I were to work-out the individual phase power, it is = V(line) * I (line).
If I am confirming the size of the 3-phase generator for the load, how would I calculate the 3-phase equivalent power?
Is it
a) P = sqrt(3) * V(line) * I(line); or
b) P = sqrt(3) * V(line-line) * I(line)
line voltage is 220, and line-line voltage is 440V. I(line) would be the calculated maximum demand any one of the lines.
Sorry, such a high-school question, but as they say, don't use it, you loose it.