It's not what you think mbrooke. Here in the US, we have a common configuration for light industrial /commercial installations where we use a 240V delta secondary with one winding, typically the A-C winding, center tapped and referenced to ground as a neutral. So you get 240V 3phase for larger loads, 240V single phase from any two legs but then for lighting and outlets, you get 120V single phase from A or C to neutral. Then on the B phase, we mark the conductor orange and call it the "High leg" or "Stinger leg" because if you try to use it for single phase to neutral, you get 208V, which stings when you fry your 120V equipment...
Jcarter12,
The problem you are running into is likely because of the size. 240/120 3phase 4wire High leg delta services are typically limited in scope to I think 150kVA, because the transformer is, by design, going to run unbalanced. A local grid with multiple 500+kVA versions presents a problem for the utility.