ajk1
Structural
- Apr 22, 2011
- 1,791
In CSA A23.3 Design of Concrete Structures, there is a Table for determining minimum thickness of beams and slabs, if deflections are not computed. There is a footnote saying that "(b) for fy other than 400 MPa, the values shall be multiplied by (0.4 + fy/ 670)". Units are metric. Similarly in ACI I believe.
Question
If I want to use 750 mm deep reinforced concrete Tee beam to span 16.3 m clear single simply supported beam, can I manipulate the expression to solve for fy as shown below?
Span/16 x (0.4+ fy/ 670) = 750
16300 / 16 x (0.4 + fy /670) = 750
Solve for fy = 225 MPa or 32,600 psi
Then calculate steel area required based on 225 MPa rather than based on the actual fy (400 MPa) of the rebar.
This gives me a required steel area of 7200 mm2 or 11.2 in2 giving a c/d ratio of 0.066 which is less than the 0.636 c/d Code limit, so OK.
Is that legitimate? Any comment?
I will of course also calculate deflection.