snowmachine88
Structural
- Jul 23, 2014
- 22
I have a slab supported on very short concrete members. The members are 3.5' from bottom of slab to top of the wall they are supported by and are 12" square. The slab is supported by a wall on one face. The slab is 56' x 33'. If I assume the slab expands due to a 45 degree temperature change and the load factor for force effects is 0.5 based on AASHTO, I get an expansion of 0.053" and 0.045" in the two perpendicular directions. Then if I assume the columns are fixed at the top and bottom I calculate end moments of 95 k-ft and 81 k-ft for orthogonal directions. I am not going to be able to design for this moment because as the column size increases so do the forces.
With a total displacement of approximately 0.07", can I assume the column will crack and relieve all of the thermal forces, or do I need to do something different to design for the thermal restrain loads?
I attached my calculations of the loads.
With a total displacement of approximately 0.07", can I assume the column will crack and relieve all of the thermal forces, or do I need to do something different to design for the thermal restrain loads?
I attached my calculations of the loads.