Hi all,
Some background: I am designing a fully composite insulated concrete sandwich panel tilt up wall panel. My situation is a 35'-0" tall panel with restraint at the footing, restraint at 5'-0" above footing into slab on grade, and restraint at the top of the panel to roof steel/diaphragm.
I am trying to back calculate the applied loading values that Thermomass System SC software is giving me with respect to temperature loads. Since I have added a slab tie per my comment above, thermal loads are causing very high moments and restraining forces to my panel.
In a panel without openings, I can come very close to matching the output of the software via hand calculations using the gross moment of inertia to calculate the restraint force at the slab level. However in my specific case I have two dock door openings and I cannot figure out how the thermal forces are modified from the solid panel condition for this case. I suspect that the overall panel moment of inertia is modified (lower) to account for the openings which would in turn reduce temperature loads as compared to a solid panel. However I am unable to back calculate how this is being done.
Would anyone be able to help me reverse engineer these calcs or understand how they may be coming up with their values? If it is helpful, I can post my hand calc to show the solid wall case that matches the software almost perfectly.
Some background: I am designing a fully composite insulated concrete sandwich panel tilt up wall panel. My situation is a 35'-0" tall panel with restraint at the footing, restraint at 5'-0" above footing into slab on grade, and restraint at the top of the panel to roof steel/diaphragm.
I am trying to back calculate the applied loading values that Thermomass System SC software is giving me with respect to temperature loads. Since I have added a slab tie per my comment above, thermal loads are causing very high moments and restraining forces to my panel.
In a panel without openings, I can come very close to matching the output of the software via hand calculations using the gross moment of inertia to calculate the restraint force at the slab level. However in my specific case I have two dock door openings and I cannot figure out how the thermal forces are modified from the solid panel condition for this case. I suspect that the overall panel moment of inertia is modified (lower) to account for the openings which would in turn reduce temperature loads as compared to a solid panel. However I am unable to back calculate how this is being done.
Would anyone be able to help me reverse engineer these calcs or understand how they may be coming up with their values? If it is helpful, I can post my hand calc to show the solid wall case that matches the software almost perfectly.