cdafd
I may do that. No fire pump. City pressures are unlikely to reach much higher than the 100psi currently seen at the riser in the basement, though of course there are always anomolies.
FFP1
I noticed the bulb wasn't centered precisely also, but the bulb I removed from the sprinkler who's seal washer and bell plug are shown in the initial post pic seemed fine. The common denominators seem to be location and what appears to be a plastic or somesuch coating coming away from the seal washer. So I would tend to think as you say that it may be a manufacturers defect.
As mentioned to cdafd, the pressures here are rarely excessive, though I can't confirm if there has been any instances of the local FD connecting a pumper to the system and pressuring up during a test run or false alarm, though this would seem imprudent.
As to the idea of an inspectors test being installed at the highest point being a solution to excessive trapped air, in a system such as this where there's two levels of "mall" and then an additional 4 stories of hotel that does not cover the whole of the mall, large volumes of trapped air is inevitable? I would respectively suggest that there could never be a system wholly devoid of trapped air though a good designer will try and mitigate this inherent problem with a good design. I've always wondered why air reliefs were never incorporated into sprinkler systems.
Thanks both for your response
Regards
Dave