The beam is too deep Mr. Engineer 2
ANE91
12-foot span supporting two residential stories, (2)14” LVLs flush, joist bays are 12’ and 16’, contractor wants 9-1/4” instead. Deflection controlled. No chance of reconfiguring the floor plan to cut down the trib width or add interior supports. I can’t think of a way to make this work…5 or 6 LVLs feels like crazytown. Any creative ideas before I crush his dreams of a mildly taller ceiling?
I’m sure there’s plenty of other posts about this exact topic, but I wanted some contemporary feedback while I searched. Thanks y’all.
Solution
Seeing a floor plan would be helpful.
Some ideas:
  1. Use a steel beam. I would bet a W8 section works for your loads and fits within the desired floor depth.
  2. Use a flitch beam (for ex. 2 LVL plies with a steel plate sandwiched between).
  3. If the floor plan allows it, push the beam up into a wall above. This only works if there aren't any wall openings which would be obstructed by the beam.
I usually go with option 1 in this situation.
Could the reason be related to providing rotational restraint at wood bearings? I know this can be done with a flange plate bolted to the wood, but that can be messy.
Rotational restraint? I'm assuming the original analysis considered the supports as pinned and free to rotate. I, too, like to have steel posts supporting steel beams, but, when I do, I weld the beam to the column (because, usually, there is no room for a cap plate) analyze the beam/columns as a frame. This not only reduces the beam size but also more correctly analyzes the column because, with rotation, there is moment.
9 out of 10 times I use a knife plate since there is no room for a cap plate. No welding required. Simple bolting.
not good at shorter spans as the end reactions are typically very high.
XR250, Could you explain the correlation between short spans and very high end reactions. That has not been what I have seen over the years.
I am generally using flitch beams on remodel projects more than new-build. Contractors I work with prefer the flitchs over the steel beams.
What about detailing it so that it's shallower than the wood, and held 1/4" to 1/2" above the bottom of the wood plies? That's my go-to...curious if you've seen issues with that approach in the wild. I haven't gotten complaints, but then I wouldn't be surprised if they just spray painted a piece of plywood black to trick a city inspector...
These has been threads about this previously. I honestly have never seen an issue but doing the math on how the load gets moved around from steel to wood makes a brain hurt.
So in the OP's case, 2 floors at 14 ft. avg. trib, the end reaction would be about 7k. Moment would be about 20 ft-k so roughly a 3/4x9 flitch. Now use that flitch in a different case where it has a 20 ft. span (say supporting a roof) , it could only take about 350 PLF before it fails in deflection and the end reaction is 3.5k - much more palatable.
Maybe I'm not visualizing it correctly, but wouldn't that connection induce moment into the column due to the eccentricity?
Thanks XR, I see what you mean now.
"For a given beam section that is loaded to the max", the shorter span ones tend to support more total load because they are generally controlled by shear rather than moment/deflection. But that is true for even steel beams, not just flitch beams.
I was thinking why would 10' at 1,000 lbs per foot have higher reactions than 20' at 1,000 lbs per foot. You are saying the shorter beam could support a higher load magnitude.
Not sure what your loads are. 7x wide might be the best option to avoid any steel. Anyway a PSL can work here? Also you stated "contractor wants".... What are his reasons? Is the Architect fine with using 14" leading to step in ceiling or it protruding down?
Very minor. I believe AISC lets you ignore any eccentricity as long as it's not an "extended" connection. A simple knife plate that's a few inches long with a single row of bolts isn't going to be an issue.
Form JS's post....
"We always show the flitch plates being shallower than the wood, but flush to the bottom. No way to transfer the shear at the end thru bolts into the columns with heavy flitches. Need the steel plates to bear directly on the PSL post and/or steel bearing plate."
I guess I'm not usually loading these to the max - I use them for longer spans where deflection controls and the end reactions are manageable through bolts. Sometimes I'll split it multiple plates to get more shear planes.
I understand AISC's position on shear tabs not required to be designed for the eccentricity, but what about the column? If the distance between the bolts and the end of the shear tab is 1-1/2", there is a 1/2" gap between the end of the shear tab and face of column and the column is 3" wide, then that's an eccentricity of 3-1/2". That doesn't seem insignificant to me.
I have no issue with any of these solutions if properly designed and detailed. I agree with everyone above.
Another solution I might be ok with is (6) 1 3/4 x 9 1/4 LVL. Just gotta make sure it's detailed to facilitate load sharing between plies, which could get expensive. Might be better to use (3) 3 1/2 x 9 1/4 LVL, or maybe an extra wide, single ply custom engineered lumber beam, depending on your specifics.
There have been many threads discussing the topic. The most recent was last June, I believe.
With respect and, in spite of those many threads which do not draw a consensus on the effects on the supporting column, I stand firm with the position that one cannot just ignore the effects of an eccentric load on a column, whether it's a shear tab connecting a steel beam to an HSS post or a face mounted hanger with concealed flanges (HUC) connecting a wood beam to a wood post. I "get it" regarding AISC's position of a steel beam considered as a simple span beam when the connection is a shear tab. There is some slop between the holes and bolts allowing some rotation.
WestFraser and Weyerhauser do not seem to list values for more than 4 plys, though.
I had a project with (6) LVLs. Depth was the issue due to an existing HVAC trunk line.
I reached out to Weyerhauser for the same reason, and one of their SE's responded that they had no prohibition on it, they just didn't include multiples that high in Forte. Same screw pattern and connections, just needed more jack studs in the beam pocket. Plus maybe a different plywood spacer to flush out.
So you didn’t do anything special to get the load into all 6? I like to imagine that, if I had something absurd and unrealistic like 60 LVLs, then there’s no way that the shear is distributed enough to mobilize what is almost a sideways wall at that point. Then there’s all the accumulated bending and possibly torsion to consider.
ANE91,
Yes, a line has to be drawn somewhere. The line will be different for each of us.
Based on some recent research I did, no, steel is not necessarily more expensive than LVL beams. I actually found it to be slightly cheaper based on comparing costs of an LVL beam with a steel beam of similar strength.
The contractor doesn't get it both ways. Let them either choose steel and the ceiling height they prefer or LVL and a deeper ceiling. There's nothing about steel that should be a deal breaker for a good builder.
I held this belief for many years that a steel beam must be supported by a steel column. After giving it more thought, I couldn't think of a good reason why. If a PSL post or other wood column has adequate capacity, why not support it on that?
Sure, here's one from a recent project where I needed a 16" LVL beam but the floor depth was only 11 7/8". I usually don't go overboard with this. For example, I probably wouldn't use something like a 24" deep beam where then it becomes questionable if the top of the beam would be laterally braced against buckling.
Out of curiosity, how did you deal with out of plane attachment/continuity through the beam in the wall? Normally I see blocking and HD's with thru-bolts or a bunch of screws in tension both sides and drags as needed.