You are right, Zogzog. The "megger test" it is not an accurate test for a cable but only an indication of insulation state
and the resistance measured is compared with a "rule of a thumb" formula as in the above standard.
The new IEEE 525/2007 revised this, I think.
The Red Book- IEEE-std 141 indicates for low voltage cable a 1000-2500 V d.c. megger test as an indication of insulation state and should be compared with an older test one in order to check the insulation degradation, if any.
See ch.12.11.9 Megohmmeter test.
Low voltage cable of 1 kV rated it seems to me meets IEC 60502-1/2004 requirements. Here in
ch.19 "Electrical tests after installation" it is mentioned:
"Tests after installation are made, if required, when the installation of the cable and its accessories has been completed. A d.c. voltage equal to 4 U0 shall be applied for 15 min.
NOTE: Electrical tests on repaired installations are subject to installation requirements. The above test is for new installations only"
Uo=600 V 4*Uo=2400 V .