Hi,
We have a problem of voltage spikes in a VFD installation (220V) with 7 induction motor fans in parallel (about 8 amps in total).
We have measured spikes in PWM pulses (50ns rise time) about 800V peak in the farthest motor from VFD.
We are assesing what to do (add reactors, dV/dt filters etc. etc.) and I found a "termination network" discussion about using RC network between phases matching the cable impedance like this:
R about 100ohms
C about some tenths of nF
Supposedly, at the pulse rise the R matches the cable impedance so spike is "cancelled", after that C charges to line value so no permanent power is wasted.
Has any sense for you guys? any experience or supplier with this kind of terminators?
I have thought that might try with three 100ohms 47nF snubber between phases to see what happens...