hswang2

Civil/Environmental
Oct 27, 2006
53
I have an ethoxylation process with temperature split range control question.

First I would like to introduce this process a little bit. The ethoxylation process is to produce non-ionic surfactants and PEG(polyethylene glycol). Fatty alcohols, or alkyl phenol are typically used as reactant with ethylene oxide. The reactor type is semi-batch liquid stirred reactor, equipped with a circulation loop to increase the reactor heat exchange capacity, and liquid EO is continuous dispersed into the gaseous one, followed by post-treatment operation such as catalyst removal to achieve the required quality of the product. The usual operation pressure in this process is 4~5 bara. Nitorgen will be purged to the reactor to assure the EO gases composition within the safety limits. Besides that, the reactor temperature is between 120 degree C to 180 degree C and is kept constant by external regulation.



This PID(TIC-120) controller to keep the reactor temperature constant. The heat removal is made by water recirculation cooler and heat addition is made by water recirculation heater. TIC-120 measures the temperature at inlet of reactor heat exchanger by the temperature transmitter TE/TIT 120 and acts on following valve,TV-120A, TV-120B and TV-120C. ( TIC -120 output and TV-120A, B and C position is on the attached pdf) TIC-001 measures the reactor bottom line temperature by TE/TIT-001 and act on set-point of 120 in cascade mode.

My question is the temperature control loop T-120.
Why do we have to set TIC-120 middle output as 50% instead of 70% to make valve action?
My reason is that the slower valve should require longer time to react.
It seems to for system take longer time to shut the TV-120A(steam valve close/open) so set TIC-120 output middle value as 70% seems more approaiate.

Thank you



 
Replies continue below

Recommended for you

hswang2,
You will probably have a reason that you entered this question. It appears to me that it isn’t just curiosity on the TIC-120 percentage setting for the valve TV-120A.

It appears to me that there are some mistyping errors in your data:
• In the table TV-120A is closed at 50% of TIC-120, which conflicts with the graphic.
• In the graphic it seems that the “TIC-120 output” and “Valve position” are mixed up.

If I understand your data correctly, following appears to happen starting with full heating:
• At 0% TIC steam is full open on the steam HX. There is no cooling by the CW HX. The valve TV-120B is fully open.
• If the temperature of the reactants at the discharge of the Reactor HX becomes too high, the TIC will give a higher value e.g. 20%. The steam supply will be reduced. Part of the water returning from the Reactor HX will be diverted to the CW HX.
• At 50% TIC there will be no steam supply. Part of the water is diverted to the CW HX for cooling and the remainder bypasses the CW HX through the valve TV-120B.
• In the range 50 … 100 % TIC the quantity of cooling is increased to full CW HX cooling at 100% TIC.

Whether a change in the closed position of valve TV-120A from 50% to 70% TIC would be beneficial, cannot be answered without detailed mass and heat balances.

You have an existing situation with HXs with a specific heat exchanging surface. An increase in TIC percentage for the closed position of TV-120A could be beneficial, if you have too abrupt cooling in the present situation, but note that flow quantities are changing.

Kind regards,
FMJalink
 
Thak you very much for your help.

I miss up the x-y axis label.
X-axis should be the valve position and
y-axis should be the TIC output

And it seems to me that I didn't
put the data right in this graph.
 
Sorry to put the same issue twice.

I make a mistake in this graph
The TIC-120A should be
close at TIC-120 output=50%, and
the green line should draw from TIC-120 output
100%(open) to TIC-120 output50%(close).


 