Temperature of air ventilated from pump room???
kmtswims
11
I am trying to figure out the temperature of the air that I am ventilating from a pump room to decide whether it needs to be exhausted to the outdoors. I have (2)20hp pumps, I have done a rule of thumb to figure out the Btuh that these will be giving off and came up with 15026 Btuh. (110 Watts per hp> (110*40=4400 Watts > converted to Btuh = 15026). I am moving 1000 cfm out of the room and intaking the same. The room is approximately 100 sq. ft.
Thanks for the reply. I am sorry, I really should have clarified that I don't have a good concept of what the intake air temperature is going to be. This room is in a ventilated garage that is partially buried underground. I am obviously trying to figure out worst case scenario. This building is in South Florida.
air temp rise = 15026/(1000*1.08)= 13.91 Deg.F
Assuming 95 Deg. Entering air, leaving air = 95 + 13.91 = 108.9 Deg.F
Hope this helps.
First, I think your heat gain from the motors is low. ASHRAE has a guideline for this, and a 20hp pump with both motor and pump in the same space releases 58,500 btu/hr. If both pumps are running, that's 117,000 btu/hr.
The air temperature rise = btu/hr divided by 1.08 x cfm.
If both pumps run continuously, this will be an extremely hot room.
Thanks for the post. I agree that the 13 degree dT seems very low for (2) 20hp pumps. Can you tell me where ASHRAE states the guideline for the pump heat gain?
108 deg temp rise? (117,000 / (1000cfm x 1.08))
Sounds pretty hot. Is that reasonable?
Ed