So I'm trying to figure out what seems like a relatively straightforward calculation here but I'm having trouble believing the results I'm finding and I'm wondering if you all would be able to provide any feedback.
I'm trying to determine the temperature increase that would occur in a Server Room if all the HVAC systems were to go offline for various periods of time. Here are the specifications:
-The room is 50"x70"x10" and begins at a temperature of 70ºF.
-A Heat Load of 100kw can be thought to be spread evenly throughout the room.
-What will the delta in temperature be after 10 minutes?
My approach was to use
Q = (M * C * (Tf - Ti)) / Time
Where:
Q = Heat Transfer Rate (Kw) = 100KW
M = Mass (kg) = 35,000ft^3 -> (991m^3) * (1.19956kg/m^3) = 1188kg
C = Specific Heat (kJ/kg ºC) = 0.7208kJ/kg ºC
Tf = Temperature Final = ?
Ti = Temperature Initial = 21.1ºC
But when I calculate it all out I'm getting 90.5ºC, which seems ridiculous for such a large room. Can that be right?
I did some research and this thread thread403-100404 seemed to be the closest thing to what I was requesting but I still have trouble believing it, somebody slap some sense into me please!
Where: