Level can be determined by head pressure, the force of gravity on the mass of liquid, which produces pressure.
A typical unit of measurement is inches of water column, that is, the pressure exerted by the height of a column of water above the measurement point. Commercial head pressure level transmitters have to use some standard pressure engineering units, one of those standard
engineering units in the US is inches of water. Others are psi or bar.
But the head pressure of a liquid of a different density than water will vary from the pressure developed by the same column height of water in proportion to the density differences.
Specific gravity is expressed as a ratio of the density of a liquid to the density of water. Hence, the level of any liquid can be expressed by measuring the head pressure in units of inches of water and dividing by the specific gravity of the liquid to get the actual level.
Level reading (inches of water) / Specific gravity = actual level
In practice, measurement is typically made by the level insturment in standard engineering units, like inches of water, and then corrected with the specific gravity factor to get the proper actual level;the correction typcially done in a read-out device, although some of the smart level transmitters can probably make the correction directly, nowadays.
In your case, a full tank is 17 feet = 204 inches.
If the tank were filled to the 204 inch level with a liquid lighter than water, the head pressure
would be less than the head pressure of water.
A level measurement with a head pressure level gauge of a full tank of a liquid with a S.G. of 0.945 would give a reading of 192.8" inches of water (204 x 0.954).
The instrument reading of 192.8" divided by the specific gravity, 0.954, provides the actual column height of 204".
Level measurements by pressure work great if
- you have access at the bottom of the tank, and that access is not the fill or unloading pipe.
Head pressure can not "see" any pressure below its own elevation., so a level transmitter mounted a foot above the bottom of the tank cannot measure below that 1" level. Flow past a pressure access tap produces error.
- the specific gravity of the liquid is constant.
Other technologies that mount from the top: no-contact like radar, ultrasonic or IR; or contact technologies like capacitive or magetostrictive are not affected by S.G. changes.