Thanx, gent on your comments; here are more details.
There are two 2500 m3 tanks i.e. pressure vessels, to be designed for liquid CO2 at 18 barg and -22 C. The Current "working" scenario is that one will be in the discharge mode with an outflow of 16 m3/h of liquid CO2, while the second one will be in the "filling" mode with max inflow of 100 m3/h 12 hours per day. Liquid CO2 will be supplied at a pressure of 16 barg and then have to be pumped to the tank/PV.
Liquid feed to the tank will be at the top of the tank.
Tanks will be provided with a condensing system for vapor, as well as an evaporator to maintain the pressure of the tank in the "discharge mode."
MAWP not decided but as low as possible to optimize cost. Especially coz there is a requirement from the client to go for low-temperature (-70 C) steel to cover the scenario of temperature drop due to a tank leak/rupture.
For the early detection of stratification, we were thinking of a "couple" thermoelements across tank height. What do you think?
There will also be a recirculation of the tank inventory possible, don't want to run the pump continuously but only if stratification is observed. What is the required recirculation rate?
If rollover happens, how much vapor generation will be, i.e., how to size PSV and condensing system?
Our current main drive for the condensing system is the filling scenario since tanks will be located in a cold climate area with "good" PUR insulation.