bipinsa
Electrical
- Apr 7, 2011
- 8
All,
All the electrical experts, please help me find out some references that talks about overall stability of the system,. Here is what I am fighting with.
We have a potential design that involves two 50MW of power generation at 13.8kv (total 100MW). This power needs to be shipped at a distance of about 1500m. and then come back at 25KV to feel the facility (several circuits). There are two options we currently have and need your opinion as to which one is the best and why?. Thanks in advance for your help;
1. First option involves a 15KV main-tie-main switchgear @ 6000 A ( I have found one) right after the generators and synchronize it and then up convert it to 260Kv (two transformers for two gens) and then ship it to the Sub (@ 260kv). This scheme gives cable and transformer redundancy. But in tshi scheme you are exporting 1005 power and then getting it back from the Sub at 25kv. There are cable losses, costs of cable...etc.
2. Second option is to step up the 13.8kv generation to 25kv and then install a local 25KV switchgear close from the generators. feel all the local 25Kv load (almost 60% of 100MW) and then transport the remaining power to the substation at 25KV. This potentially adds two distribution buildings (one is the SUB an done is this 25KV SWGR). This will now require more relaying and communication with the SUB.
In option one the generators are synchronized before the step-up transformers at 13.8kv and in option two the generators are synchronized after the step-up transformers. I need to understand which choice is a better one and which system would be more stable. I have done skm studies and fault level calculations. can some one throw their experience on system stability, generator system grounding with respect to each option. Any references or documents will be highly appreciated. Thanks,
All the electrical experts, please help me find out some references that talks about overall stability of the system,. Here is what I am fighting with.
We have a potential design that involves two 50MW of power generation at 13.8kv (total 100MW). This power needs to be shipped at a distance of about 1500m. and then come back at 25KV to feel the facility (several circuits). There are two options we currently have and need your opinion as to which one is the best and why?. Thanks in advance for your help;
1. First option involves a 15KV main-tie-main switchgear @ 6000 A ( I have found one) right after the generators and synchronize it and then up convert it to 260Kv (two transformers for two gens) and then ship it to the Sub (@ 260kv). This scheme gives cable and transformer redundancy. But in tshi scheme you are exporting 1005 power and then getting it back from the Sub at 25kv. There are cable losses, costs of cable...etc.
2. Second option is to step up the 13.8kv generation to 25kv and then install a local 25KV switchgear close from the generators. feel all the local 25Kv load (almost 60% of 100MW) and then transport the remaining power to the substation at 25KV. This potentially adds two distribution buildings (one is the SUB an done is this 25KV SWGR). This will now require more relaying and communication with the SUB.
In option one the generators are synchronized before the step-up transformers at 13.8kv and in option two the generators are synchronized after the step-up transformers. I need to understand which choice is a better one and which system would be more stable. I have done skm studies and fault level calculations. can some one throw their experience on system stability, generator system grounding with respect to each option. Any references or documents will be highly appreciated. Thanks,