- May 16, 2007
- 482
Hello,
I can use some advice on a generator problem. I have a synchronous generator 10MW, 13.8kV. About a month ago, the plant had a shutdown, and afterwards they couldn't get on line because the generator couldn't build enough voltage. We got to about 9.4kV. The rotor was pulled out and checked out. No problems have been found in the rotor. The field current used run at 117A to get the stator voltage to 13.8kV. Now we need 150A to get to 9.4kV. Has anyone encountered such a problem, and can you give me a head start on what to look for?
thanks
I can use some advice on a generator problem. I have a synchronous generator 10MW, 13.8kV. About a month ago, the plant had a shutdown, and afterwards they couldn't get on line because the generator couldn't build enough voltage. We got to about 9.4kV. The rotor was pulled out and checked out. No problems have been found in the rotor. The field current used run at 117A to get the stator voltage to 13.8kV. Now we need 150A to get to 9.4kV. Has anyone encountered such a problem, and can you give me a head start on what to look for?