A couple of comments on day top day operation of a small plant that may make the operation a little clearer.
The old plant that I was most familiar with had an operating sequence something like this.
1> The load is less than 300 KW, one 350 KW set is online.
As the load changes the operator may adjust the speed setting if he notices that the frequency is off 60 Hz.
2> The load is up to about 300 KW. Another 350 KW set is placed online.
A> The second 350 KW set is started and the governor speed control is adjusted until synchronism is achieved. The breaker is closed. Both sets are now locked together at the same frequency but the second set is not carrying any load.
B> The operator now increases the speed setting of the second set. The set starts to pick up the load. As it does, the first set is proportionately unloaded and both sets speed up slightly. The operator will probably reduce the speed setting of the first set, until the load is shared equally by both sets. Now both speed controls may be moved in the same direction if needed to get closer to 60 Hz.
From time to time, if the operator notices the frequency dropping a little with a load increase, he may increase the speed settings of both sets slightly to get back to 60 Hz.
With the load evenly distributed on both sets, the speed setting will be the same. Now the sets will share any load variations.
C> As the load gets up over 600 KW a 900 KW set is started, synchronized and put online. The speed setting of each 350 Kw set is reduced until it is at a no load condition and it is taken off-line and stopped. As this is being done, the speed control of the 900 KW set will be tweeked to maintain the frequency at 60 Hz.
D> The load is over 800 KW and climbing. A 350 KW set is started and synchronized. Total capacity on-line is now 350 KW + 900 KW = 1250 KW. The governors are now adjusted until the load is shared in the ratio of 350KW/1250KW to 900KW/1250KW. Both governors are tweeked to bring the frequency close to 60 Hz. The sets will now share load fluctuations in proportion to their ratings.
There is no indiction for exact speed setting. Typically there will be a three position, return to center switch on the switchboard. Turn to the left, reduce speed. Turn to the right, increase speed. Spring return to center, off.
The speed is adjusted by balancing the proportion of the load between the sets, and watching the frequency. The operators don't know what the no-load setting may be, but they don't have to know to do their jobs. They do know that the load is shared in the correct proportion, and that the frequency is close to 60 Hz. That's all they need to know.
The operators read and record a number of parameters every 15 minutes. Volts, Amps, Oil Pressure, Coolant Temperature etc.
An option is to use a crystal controlled clock and an old synchronpus motor driven clock and compare the times to fine tune the frequency. The small utility that I am describing didn't bother with this refinement.
By the way, when I first started encountering generators, I didn't see one often enough to justify the purchase of a frequency meter.
I have set the frequency many times with an old electric clock and the second hand on my wrist watch. Alas, the synchronous motor drive clocks seem to be all gone and I now make sure that any multi meter that I buy has a frequency function. I haven't used a clock for about 15 years now and, come to think of it, I haven't seen a suitable clock for about 15 years.
respectfully