I know that for applying a PT on a 4.16kV impedance grounded system (non-rigidly grounded)the PT needs to be a 2400/4160Y PT as opposed to a 2400/4160GY PT due to the fact that the neutral bushing needs to be a fully rated bushing for when neutral floats to line voltage during certain fault conditions.
I have 2 questions here:
1) What is the L-G rating of the bushings on a 2400/4160Y PT? I believe they are only 2400V but wouldn't they need to be 4160V if L-N voltage can be elevated to L-L voltage during certain fault conditions?
2) In a 2400/4160Y PT I understand the winding to be rated at 2400V. If PT is connected L-N then during certain ground fault conditions the PT winding will see L-L voltage of 4160V. Can the PT winding sustain this temporary overvoltage or must a 4160/4160GY PT be used? I'm not familiar much with these but understand that during normal conditions they are meant to operate at 58% rated voltage and thus during ground fault would only see the voltage rating of the primary winding?