Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Sync Diesel Generators

Status
Not open for further replies.

NuTech

Mechanical
Joined
Oct 9, 2001
Messages
2
Location
IN
I have 2 Diesel Generators, each having a generation capacity of 125 KVA. Is it possible to drive a load of 200 KVA using these 2 geneerators.

In effect what i want to know is that can a feed the supply from the two generators into a common busbar and then drive the load from the busbar.
 
It may be possible to supply a 200 kva load with the two 125 kva Diesel generators, but that depends on the specific nature of the load and the actual capabilities of the Diesel generators. You will need proper synchronizing switchgear and appropriate protective equipment.

The two Diesel generator control systems need to have compatible characteristics. They should share the loading without one becoming overloaded.

What is the nature of the load. Is it several small loads that can be started in a controlled sequence? If so, the proposed system is likely to work. Is it one induction motor with a running load of 200 kva? If so, it is nearly certain that the motor would never be started.

If the proposed system is to be implemented, you would do well to hire competent engineers for this project.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top