How this is done if we have to synchronize two different sources from Utility?
Hmmm; the replies so far have been interesting, to say the least . . .
Power from two utilities in the same system will be inherently synchronized.
I must agree with Fischstabchen here; it ain't necessarily so.
You may need a phase shifting transformer to control the direction of power flow.
This would work, but it would have to be equipped with under load tap changers, and these types of transformers are a truly expensive piece of kit.
The OP did not specifically mention interconnecting two utilities, so the way I initially read the question was to parallel two different sources from the same utility . . . but I may have been wrong.
If in fact interconnecting sources from two utilities or grids was actually intended, Bill's suggestion of using some manner of asychronous tie would work very well and pose no major technical issues; all AHJs would have to be on board with this, though, and getting the required approvals could be a tough sell. The same proviso would apply to use of a phase shifting transformer.
As to directly connecting such sources, I would answer that other than in extremely exceptional circumstances, this is something you should never, not ever, not even in your wildest dreams, ever think of doing, for the following reasons:
If in fact there is already some other path of interconnection between the two utilities in question, there may well be a standing connection of some fixed phase angle across the device you wish to close.
If those two standing-angle sources are in fact already in phase, when this connection is made there will be two parallel paths by which grid power will flow; the division of power flow between them will be inversely proportional to the impedances of the two paths, and generation dispatch on the grids will have a material effect on such flows as well.
As a result, you site may well serve as a transfer path for very high system power flows, in other words your equipment may be heavily overloaded with a power flow that dose not benefit you at all as a customer.
If the standing angle sources are not in phase, a phase shifting transformer may be required to get them into phase; see above.
If there are two unsynchronized utilities and you parallel these via your system, any generation or load mismatch between the two systems will attempt to equalize itself through your switchgear; not a pretty prospect.
CR