Live2learn
Electrical
- Jun 9, 2010
- 29
I have two utility feeds from 1500kVA transformers that terminate in new switchboard with LVPCB
Also generator paralleling gear with 1200kVA worth of generator. The generators (3) sync up and parallel with each other and then terminate on new main switchboard.
The main question lies with a closed transistion return from gen to utility. My concern that this isn't a switchgear but a switchboard. It has LVPCB's and I have rated the fault current for the combination of both services. The sources will sync up inside the gear for 100ms or less with a make before break scenarion. I am also installing new relays for better control.
Also generator paralleling gear with 1200kVA worth of generator. The generators (3) sync up and parallel with each other and then terminate on new main switchboard.
The main question lies with a closed transistion return from gen to utility. My concern that this isn't a switchgear but a switchboard. It has LVPCB's and I have rated the fault current for the combination of both services. The sources will sync up inside the gear for 100ms or less with a make before break scenarion. I am also installing new relays for better control.