Well, now comes the bad news...
~2000A @ 480V and you are looking at a different kind of beast. I've seen (and worked on) switches of this rating, also known as "bolted pressure" switches, "bolt lock" switches, or "pringle" switches. I would not recommend these and shake my head whenever I see them. Operational and maintenance nightmares, which generally have unique traits such as not opening, not closing, falling apart during operation, etc. I've only seen these applied in lieu of a main breaker, and as such don't get a whole lot of use, other than when one of it's fuses blows and the shunt trip coil burns out (failing to open switch), single phasing all motors in a building, etc...
There may be other options available, but this is what I have seen in the ratings you are looking at. I have seen these switches up to 4000A, with 100kA fuses.
If you have to utilize something like this, I would strongly suggest a regular maintenance program on the switch that includes regular and proper operation, lubrication and exercise of the switch. It is the lack of exercise and proper lubrication that generally causes the problems with these devices.
At these ratings, I would personally want a breaker. If you have the ability to isolate the 480V source upstream of the switch, this makes maintenance and repairs of the switch much easier and SAFER. My experience with these has been when they are the secondary main from a utility owned transformer, generally in light industrial or commercial applications, with one side of the switch being energized...