KWman
Electrical
- Oct 30, 2004
- 9
Do you have any case studies or equipment solutions that might be effective on correction of a severe resonance initiated by transformer inrush? The application is a commercial data center with two incoming 20 mVA transformers 34.5 kV / 12 kV, and distribution network consisting of 20 area subs 12 kV to 480 V sized 2500 to 4000 kVa.
Extended inrush as long as 25 to 40 seconds is observed as 400 amperes at the 34.5 kV service, when energizing one of the transformers, with or without minor load pickup. There is a very loud audible signature during the event... very extended inrush sound. It even occurs when energizing one of the area subs. There is voltage sag of 8% or so, and significant voltage harmonic distortion.
The 12 kV Wye secondary may be ungrounded (due to a screw up), which is one enable for ferroresonance. I'm also looking into the short circuit MVA of the utility and if there are any cap banks on their lines (none on the subject site.)
After the extended transient, system is normal and can operate critical load brought on line, such as chiller VFD and computer UPS loads.
Ever seen anything like this? Any papers or references you can direct me to? Any good literature search services you recommend?
Extended inrush as long as 25 to 40 seconds is observed as 400 amperes at the 34.5 kV service, when energizing one of the transformers, with or without minor load pickup. There is a very loud audible signature during the event... very extended inrush sound. It even occurs when energizing one of the area subs. There is voltage sag of 8% or so, and significant voltage harmonic distortion.
The 12 kV Wye secondary may be ungrounded (due to a screw up), which is one enable for ferroresonance. I'm also looking into the short circuit MVA of the utility and if there are any cap banks on their lines (none on the subject site.)
After the extended transient, system is normal and can operate critical load brought on line, such as chiller VFD and computer UPS loads.
Ever seen anything like this? Any papers or references you can direct me to? Any good literature search services you recommend?