I concur with jtkirb;
In different words;
Active Power;
This is what you pay for on your power bill. Kilo-Watt Hours
Reactive Power (Lagging). This is caused by the magnetising current of transformers, motors, and other induction loads.
Reactive power
This causes an increase in Current but no increase in work done.
This increased current causes increased heating in wires and transformers.
Reactive power is measured in Kilo-Volt-Amp-Reactive-Hours, or KVARHrs.
The power company will use a formula to compare this to the Kilo-Watt Hours and if the result is too high, they will charge you a penalty.
There is another type of Reactive Power.
Reactive Power (Leading). This is caused by capacitors and will cancel Reactive Power (Lagging)
Look at your power bill and if you are paying a penalty for reactive power, or power factor, have a professional install a capacitor bank to correct it.
The last correction that I did paid for itself in about 40 days. This was much better than usual, but typical pay-back times are almost nearly always less than a year. 8 to 10 months is typical.