If you only need a neutral to power the SMA, then use three small transformers connected in Wye/Delta.
The wye voltage must be greater than 58% of the line to line voltage and the secondary voltage is unimportant.
Connect the secondary in delta and forget it.
Connect the primary in wye and connect it to the three incoming phases. The wye point will develop a stable neutral voltage.
Do not ground the wye point. Connect it only to the SMA.
If the wye point is grounded a ground anywhere on the local system will burn out the transformers.
Transformer size?
Full load current of the primary windings to be over half the control current demand of the SMA.
Bill
--------------------