I'm not sure I would be too quick to write off e-m relays. They do have advantages - longevity, especially in some hostile environments for starters. Electronic relays just don't seem to last as long - we've still got PBO and similar relays dating back to the early '50s that are still going strong, and we are already replacing some electronic relays after only 15 or 20 years service. It's a case of being prepared to accept the trade-off of lower maintenance costs, much improved functionality and short life of electronic relays against the long life, simplicity and independence from computers of e-m.
Training, setting, installation and commissioning are also factors to consider vis-a-vis the skill sets of the people doing the work. The young guns with no instrument repair skills may struggle with e-m, but may be happy using a computer to drive everything. Older people with an instrument fitter type of background may be better off with e-m and avoiding the computers. Horses for courses.
Some of the problems we have had with numeric realys have had me wondering sometimes if they are all they're cracked up to be. But then, they have proved themselves very useful on occasions.
My perfect relay - a CDG with built in fault waveform recorder!
Bung
Life is non-linear...