Thank you for the clarification on your question. The answer is yes, there will certainly be an effect of paralleled or bundled conductors, although probably less than you may be worried about. I would:
Search and read "ATC Substation Equipment Ampacity Ratings", document # CR-0063. Published by American Transmission Company. Section 12 covers bare conductors. Section 12.7, Table 18 for specifics to you. You'll find that unless you have large conductors spaced very tight (4" or less), the effect is negligible. For your spacing: look at manufactures like SEFCOR, will the conductor and connectors you are likely to use be that close? If so, I would then get a copy of IEEE 738 and it will walk you through calculating values. There is also software, I think SKM and ETAP have modules that will assist.
I have a document from aluminum association (somewhere) that may have a lot of the same info as IEEE 738. I will look for it.