Curious as I don't have access to that design guide, what sorts of pile cap configurations/failure modes are they referring to? Wondering if that's for smaller scenarios (e.g. 2 or 3 piles) or larger pile cap groupsCRSI Design Guide for Pile Caps say that strut and tie model is unconservative for pile caps because other modes of failure can control.
Can you post a sketch ? Is the question is for STM design of pile cap ? Or pedestal ?an example of a strut and tie design for pilecap with axial load as well as shear load at top of pedestal?
If the compression strut is confined with plain concrete , ( as the case in pile caps ) , the compression stress should be limitedIt begs to ask the question are all the pile caps that we have designed without bursting reinforcement not fit for purpose?
AFAIK , the truss model studied almost a century ago and improved by MÖRSCH in 1909 . The model is called Ritter - MÖRSCH truss model. ( I have an old concrete book states this ( Vorlesungen über Massivbau by LEONHARDT ).However, I cant seem to find the history of STM and why its model has continuously changed. Are there any pile caps or deep transfer beams/walls that failed because of node failure or bursting strut failure?
- In case of deep pile caps , ( the strut confined by plain concrete ) ,The compression stress shall be limited to avoid transverse splitting/ bursting in concrete. The strut is bottle shaped. The following figure is copy and paste from ACI 318-11HTURKAK, with bursting, was looking into this a while ago and noticed end result for pilecaps was generally not to allow for bursting reinforcement
The ACI paper in post #5 mentioned confinement by plain concrete
Have you come across any other reference that elaborates on this also, reason I ask is that some do allow for bursing reinforcement
Paradoxically for a narrow column there is no plain concrete to confine, but bursting not an issue since since AS 3600 for example says it's a prsimatic compression field. But if you did add plain conrete around wouldn't the stress field diverge?
I would go a step further and suggest that a good majority of nonflexural concrete elements are still not properly designed using S&T principles (at least from what I have seen).It begs to ask the question are all the pile caps that we have designed without bursting reinforcement not fit for purpose?
This is actually a good point. Also bursting mode of failure is likely dependent on the slenderness of the strut, but this is never mentioned on STM. just cant imagine a very short plain concrete pedestal with a massive concentrated point load failing via bursting mode. Probably require more guidance from engineers in this subject, at the moment its all very vague.Paradoxically for a narrow column there is no plain concrete to confine, but bursting not an issue since since AS 3600 for example says it's a prsimatic compression field. But if you did add plain conrete around wouldn't the stress field diverge?
Had this same thought once too because I was creating a worksheet for 3/4 pile cap configurations and realised I'd never seen a pile cap with bursting reinforcement in my life. Meanwhile thinking through the bursting scenario in 3 dimensions, you'll need to install more directions of reinforcement than most would think to cover both directions of bursting for the strut.It begs to ask the question are all the pile caps that we have designed without bursting reinforcement not fit for purpose?
I have long held the view that many structures around us only work because of the generous load factors slapped on top of them and that too many structural engineers are basically none-the-wiser about it. I suspect that if tested to failure, many of these structures would exhibit a lot less strength (and just as importantly, ductility) than what the designer had intended.
Is this just saying that the bursting stresses need to remain less than the cracking stress? That's a potentially woefully small amount of capacity relative to the load you'd want to applyIn case of deep pile caps , ( the strut confined by plain concrete ) ,The compression stress shall be limited to avoid transverse splitting/ bursting in concrete. The strut is bottle shaped. The following figure is copy and paste from ACI 318-11
Should have mentioned I'm working to australian codes, interesting that we don't seem to have anything regarding restrained vs unrestrained strutsI would think you can consider struts restrained per 23.5.3 and not add bursting reinforcement for most pile cap designs