You say that you're supposed to design the "board up". Does that just mean the 27 ga. green sheet? Or are you to analyze the whole system? (concrete foundation, rebar "brace", the purlins, and the pipe)
Assuming you mean the latter, the general workflow is:
- figure out your geometry such that you can start determining loads.
- determine your loads
- apply your loads to the features that receive those loads
- chase those loads through the system into the ground (this is where knowing how the structure will behave comes in).
In your case, the wind blows (could be from L-R, or R-L, so you'll need to check both directions) on the green sheet - likely checked via a manufacturer's specification sheet. Green sheet is connected to the purlins at some spacing, load is transferred to the purlins at these location, likely a bolt or a screw - connector needs to be checked for the load. Looks like the purlins are going to transfer the wind load to the pipes via weak axis bending and shear - purlins to be checked for those internal forces. Purlins are connected to the pipes, check the connection. Pipes are now loaded, and here's where things get funky:
- is the concrete foundation only to resist sliding, or is it sized to take over-turning moment?
- how often is the rebar "brace" occurring? I have doubts of the rebar's compressive capacity at 2+ meters of length. Unless they're absolutely huge.
After that, you need to size your foundations for whatever reactions forces you need them to take. (The soil-nail rebar embed detail seems dubious to get to calc out.. you may need to call for a field load test to show that you have enough capacity.)
This is the 30,000 ft view. There's all kinds of little bits inside of each of those steps. When I was a new engineer, I was given tasks and let loose to figure it out on my own, but my boss/mentor was also reviewing what I was doing at the end of each day. Hopefully whoever gave you this task is going to be over your shoulder, pointing/pushing/nudging you in the right direction.
On the other hand, if this just something that you're supposed to whip out because it's "not a big deal, it's just a stupid view blocker", then you need to push back that you don't have the necessary experience for this.