Here's some text from AISC's Code of Standard Practice. Note the highlighted text in blue below:
4.4. Approval
Except as provided in Section 4.5, the Shop and Erection Drawings shall be
submitted to the Owner’s Designated Representatives for Design and
Construction for review and approval. These drawings shall be returned to the
Fabricator within 14 calendar days. Approved Shop and Erection Drawings
shall be individually annotated by the Owner’s Designated Representatives for
Design and Construction as either approved or approved subject to corrections
noted. When so required, the Fabricator shall subsequently make the corrections
noted and furnish corrected Shop and Erection Drawings to the Owner’s
Designated Representatives for Design and Construction.
[red]Commentary:
As used in this Code, the 14-day allotment for the return of Shop and Erection
Drawings is intended to represent the Fabricator’s portal-to-portal time. The
intent in this Code is that, in the absence of information to the contrary in the
Contract Documents, 14 days may be assumed for the purposes of bidding,
contracting and scheduling. A submittal schedule is commonly used to facilitate
the approval process.
If a Shop or Erection Drawing is approved subject to corrections noted,
the Owner’s Designated Representative for Design may or may not require that
it be re-submitted for record purposes following correction. If a Shop or
Erection Drawing is not approved, revisions must be made and the drawing resubmitted
until approval is achieved.[/red]
4.4.1. Approval of the Shop and Erection Drawings, approval subject to corrections
noted and similar approvals shall constitute the following:
(a) Confirmation that the Fabricator has correctly interpreted the Contract
Documents in the preparation of those submittals;
(b) Confirmation that the Owner’s Designated Representative for Design has
reviewed and approved the Connection details shown on the Shop and
Erection Drawings and submitted in accordance with Section 3.1.2, if
applicable; and,
(c) Release by the Owner’s Designated Representatives for Design and
Construction for the Fabricator to begin fabrication using the approved
submittals.
[blue]Such approval shall not relieve the Fabricator of the responsibility for either the
accuracy of the detailed dimensions in the Shop and Erection Drawings or the
general fit-up of parts that are to be assembled in the field.
The Fabricator shall determine the fabrication schedule that is necessary to meet the requirements of the contract. [/blue]
[red]Commentary:
When considering the current language in this Section, the Committee sought
language that would parallel the practices of CASE. In CASE Document 962,
CASE indicates that when the design of some element of the primary structural
system is left to someone other than the Structural Engineer of Record, “…such
elements, including connections designed by others, should be reviewed by the
Structural Engineer of Record. He [or she] should review such designs and
details, accept or reject them and be responsible for their effects on the primary
structural system.” Historically, this Code has embraced this same concept.
From the inception of this Code, AISC and the industry in general have
recognized that only the Owner’s Designated Representative for Design has all
the information necessary to evaluate the total impact of Connection details on
the overall structural design of the project. This authority has traditionally been
exercised during the approval process for Shop and Erection Drawings. The
Owner’s Designated Representative for Design has thus retained responsibility
for the adequacy and safety of the entire structure since at least the 1927 edition
of this Code.[/red]